  • VAV vs VVT | HVAC-Talk: Heating, Air Refrigeration Discussion
    VVT is variable Volume temperature, The VVT system relies heavily upon all the distributed zones having similar conditions It is a cheap setup IMO to provice any heat to an area it must stop cooling the others We are not talking about dual duct roght ? VAV controls cooling by controling the volume of air,this also has problems
  • linking CCN VVT to RTU Opn and UPC Open - HVAC-Talk
    Hi, Existing zones controllers are CCN VVT(part# 33ZCVVTZC-01 v1 2) We just changed out the carrier package units some has Carrier RTU open bacnet card and others has bacnet UPC open The old package units had a premierlink I've just upgraded the front end from a 4 2 appliance to IVU
  • Power Exhauster on CV -VVT RTU - HVAC-Talk
    I've got a problem, I'm not getting any air flow to ducts (minimal), Actuators are wide open and RTU is running fine this is a CV system with VVT control I noticed the power exhauster blowing out a lot of cold air, so I'm guessing that possibly the bypass is open Any guesses of possibilities
  • Carrier VVT help - HVAC-Talk
    VVT is one of my weaknesses I have never install or had any training I know there are different generations Does anyone have a cheat sheet of sorts for troubleshooting? I have a no heat call tomorrow and I'm the second Tech going into look I think it is Parker? But not sure
  • Carrier iVu RTU open factory application programs - HVAC-Talk
    Can anyone share the factory password or the factory option to access the carrier rtu open, VVT, and VAV canned programs in snap? Not trying to modify the program, I just want to be able to see the programming logic in snap
  • 75F controls | HVAC-Talk: Heating, Air Refrigeration Discussion
    Our company looked at them for a while Business Development team liked to use hot button terms like IOT, cloud and optimization Looking into them their cloud optimization seems to only be auto PID tuning which isnt that special IMO anymore Only thing I told my boss that I saw this for was for revitalizing and retrofitting VVT systems
  • Controls Manufacturer Comparison | HVAC-Talk: Heating, Air . . .
    Now there is a unitary controller that also the same hardware becomes VVT VAV It has simultaneous BACnet,LON,Modbus,OPC, OPC UA, SNMP available Who has a VAV or Unitary that is multi-protocol at that level? Who has the same device with a built in MSTP-IP router?
  • What approach would you take on VAV reheat coils that. . .
    The balancer identified this as a VVT system which is a lot different than variable volume VAV The VVT does not read airflow and airflow is set by establishing the damper set point percentage that correspond to the as balanced airflow which is only good at the static pressure during balance If the static pressure changes so will the airflow